Q01
The maximum total cable length of a line segment using certified KNX TP cable is 1000 m.TrueFalse4. KNX Installation· bus-cables· EasyQ02
What is the maximum number of bus devices per line guaranteed by the certified KNX TP cable?- A.256 devices
- B.128 devices
- C.64 devices
- D.1000 devices
4. KNX Installation· bus-cables· EasyCorrect answerA — 256 devicesLearning tipCorrect: The standardized cable guarantees a maximum of 256 bus devices per line.
Source: KNX Basic Course Documentation — 2 — p. 98Q03
What is the test voltage of the YCYM 2x2x0.8 bus cable according to EN 50090?- A.2.5 kV
- B.4 kV
- C.6 kV
- D.0.6 kV
4. KNX Installation· bus-cables· MediumCorrect answerB — 4 kVLearning tipCorrect: YCYM 2x2x0.8 has a test voltage of 4 kV per EN 50090.
Source: KNX Basic Course Documentation — 2 — p. 98Q04
What is the test voltage of the J-Y(St)Y 2x2x0.8 cable according to EN 50090?- A.4 kV
- B.1.0 kV
- C.2.5 kV
- D.6 kV
4. KNX Installation· bus-cables· MediumCorrect answerC — 2.5 kVLearning tipSource: KNX Basic Course Documentation — 2 — p. 98Q05
In the used wire pair of the KNX bus cable, red is plus and black is minus.TrueFalse4. KNX Installation· bus-cables· EasyCorrect answerTrueLearning tipThe text states the used wire pair is red for plus and black for minus.
Source: KNX Basic Course Documentation — 2 — p. 99Q06
The spare wire pair (white/yellow) of the KNX bus cable may be used for which of the following?- A.A second KNX TP data signal
- B.A DC SELV supply, or left with no connection at all
- C.Voice communication
- D.A 230 V AC mains supply
4. KNX Installation· bus-cables· MediumCorrect answerB — A DC SELV supply, or left with no connection at allLearning tipCorrect: Permitted uses are no connection at all or a DC SELV supply.
Source: KNX Basic Course Documentation — 2 — p. 99Q07
Which cables can be certified with the KNX logo by KNX Association?- A.Only cables coloured green, regardless of their electrical properties
- B.Any 230 V mains cable of adequate cross-section
- C.Cables fulfilling the KNX requirements in volume 9 of the KNX Specifications, e.g. YCYM 2x2x0.8 or J-Y(St)Y 2x2x0.8 in TP design
- D.Only cables tested to 6 kV
4. KNX Installation· bus-cables· MediumCorrect answerC — Cables fulfilling the KNX requirements in volume 9 of the KNX Specifications, e.g. YCYM 2x2x0.8 or J-Y(St)Y 2x2x0.8 in TP designLearning tipCorrect: These meet the volume 9 requirements and can carry the KNX logo.
Source: KNX Basic Course Documentation — 2 — p. 98Q08
How should the shielding of KNX bus cables be treated regarding the equipotential bonding bar?- A.It must be bonded to the equipotential bar at every device
- B.It must be earthed at the power supply only
- C.It must be connected to the protective earth of the mains
- D.It may not be connected to the equipotential bonding bar
4. KNX Installation· bus-cables· MediumCorrect answerD — It may not be connected to the equipotential bonding barLearning tipCorrect: The shielding of the bus cables may not be connected to the equipotential bonding bar.
Source: KNX Basic Course Documentation — 2 — p. 98Q09
A terminating resistor is not required in a KNX TP installation.TrueFalse4. KNX Installation· bus-cables· EasyCorrect answerTrueLearning tipThe documentation states plainly that a terminating resistor is not required.
Source: KNX Basic Course Documentation — 3 — p. 101Q10
On which DIN rails may KNX TP DIN-rail mounted devices be installed in a distribution board?- A.Standardized EN 50022 35x7.5 mm DIN rails
- B.Only proprietary KNX rails supplied by the manufacturer
- C.EN 50090 15x5 mm rails
- D.Only earthed metal rails used as the SELV return
4. KNX Installation· bus-cables· MediumCorrect answerA — Standardized EN 50022 35x7.5 mm DIN railsLearning tipCorrect: Any commercial board with EN 50022 35x7.5 mm DIN rails may be used.
Source: KNX Basic Course Documentation — 4 — p. 101Q11
In a KNX TP installation, the maximum permitted length of a single line segment is 1000 m.TrueFalse4. KNX Installation· installation-check· EasyQ12
In a KNX TP line, what is the maximum permitted distance between the power supply unit and a bus device?- A.700 m
- B.1000 m
- C.350 m
- D.As specified by the manufacturer
4. KNX Installation· installation-check· MediumCorrect answerC — 350 mLearning tipCorrect: The distance between the power supply unit and a bus device may not exceed 350 m.
Source: KNX Basic Course Documentation — 17.1 — p. 118Q13
During the installation check, how should the ends of the bus cables be marked?- A.'KNX TP' or 'BUS'
- B.With '230 V' to warn of the operating voltage
- C.No marking is required at the cable ends
- D.With the manufacturer's serial number only
4. KNX Installation· installation-check· EasyCorrect answerA — 'KNX TP' or 'BUS'Learning tipSource: KNX Basic Course Documentation — 17.2 — p. 118Q14
Which statement about connecting the bus cables of different lines is correct?- A.Bus cables from different lines may be connected at the line coupler.
- B.Bus cables from different lines may never be connected together.
- C.Bus cables from different lines may be connected if the total length stays under 1000 m.
- D.Bus cables from different lines must be connected to form a single segment.
4. KNX Installation· installation-check· EasyCorrect answerB — Bus cables from different lines may never be connected together.Learning tipCorrect: Bus cables from different lines may never be connected together; the check looks for such inadmissible connections.
Source: KNX Basic Course Documentation — 17.3 — p. 118Q15
The insulation resistance of the bus cable shall be at least 500 kΩ.TrueFalse4. KNX Installation· installation-check· EasyCorrect answerTrueLearning tipCorrect. The insulation resistance of the bus cable shall be at least 500 kΩ.
Source: KNX Basic Course Documentation — 17.4 — p. 119Q16
At what test voltage should the insulation resistance of the bus cable be measured?- A.250 V DC
- B.230 V DC
- C.500 V DC
- D.21 V DC
4. KNX Installation· installation-check· MediumCorrect answerA — 250 V DCLearning tipCorrect: The insulation resistance measurement should be carried out at 250 V DC.
Source: KNX Basic Course Documentation — 17.4 — p. 119Q17
Why should overvoltage protectors be removed before measuring the insulation resistance of the bus cable?- A.Because overvoltage protectors are only fitted on mains cables, never on bus cables.
- B.So the measurement is not influenced and the overvoltage protector is not damaged.
- C.To raise the test voltage above 250 V DC.
- D.Because the protectors must be replaced after every insulation test.
4. KNX Installation· installation-check· MediumCorrect answerB — So the measurement is not influenced and the overvoltage protector is not damaged.Learning tipCorrect: Overvoltage protectors should always be removed before the test so that the measurement is not influenced and the protector is not damaged.
Source: KNX Basic Course Documentation — 17.4 — p. 119Q18
What is the minimum bus voltage that must be measured at the end of each bus cable?- A.24 V DC
- B.29 V DC
- C.20 V DC
- D.21 V DC
4. KNX Installation· installation-check· MediumCorrect answerD — 21 V DCLearning tipCorrect: The bus voltage at each bus cable end should be at least 21 V DC.
Source: KNX Basic Course Documentation — 17.6 — p. 119Q19
When the ETS project is handed over, the customer's signature confirms agreement with which of the following?- A.Only the total price of the installation.
- B.All the realized functions, and that the installer's warranty expires with any change to the realized KNX installation.
- C.That the installer stays liable for any future changes made by others.
- D.That no project documentation needs to be provided.
4. KNX Installation· installation-check· MediumCorrect answerB — All the realized functions, and that the installer's warranty expires with any change to the realized KNX installation.Learning tipCorrect: With the signature the customer agrees to all realized functions and that the installer's warranty expires with any change to the installation.
Source: KNX Basic Course Documentation — 17.8 — p. 119Q20
In the sequence for checking a KNX installation, which check is carried out immediately after checking the polarity of all bus devices?- A.Measuring the insulation resistance of the bus cables
- B.The visual check of the bus cable-end marking
- C.Measuring the bus voltage at each bus cable end
- D.Recording the test results
4. KNX Installation· installation-check· MediumCorrect answerC — Measuring the bus voltage at each bus cable endLearning tipCorrect: The polarity check is followed by measuring the bus voltage (minimum 21 V) at each bus cable end.
Source: KNX Basic Course Documentation — 17 — p. 118Q21
In a common installation box with a partition, what clearance and creepage distance does the source require between mains and bus?- A.2,5 mm.
- B.8 mm.
- C.5,5 mm.
- D.0,5 mm.
4. KNX Installation· connectors-and-mounting· MediumCorrect answerC — 5,5 mm.Learning tipCorrect: the source requires 5,5 mm clearance and creepage distances.
Source: KNX Basic Course Documentation — 8 — p. 108Q22
How should flush-mounted bus devices be fixed in the wall box?- A.By clamp mounting, which is the normal method for bus devices.
- B.Screw or clamp mounting; either works equally well.
- C.By gluing the device into any available box.
- D.In wall boxes suitable for screw mounting; clamp mounting is usually not possible.
4. KNX Installation· connectors-and-mounting· EasyCorrect answerD — In wall boxes suitable for screw mounting; clamp mounting is usually not possible.Learning tipCorrect: only wall boxes suitable for screw mounting may be used.
Source: KNX Basic Course Documentation — 9 — p. 109Q23
On the standardized KNX TP bus connector, which statement about the two parts is correct?- A.The plus part is red and the minus part is black.
- B.The plus part is red and the minus part is dark grey.
- C.The plus part is black and the minus part is red.
- D.Both parts are green, matching the bus cable sheath.
4. KNX Installation· connectors-and-mounting· MediumCorrect answerB — The plus part is red and the minus part is dark grey.Learning tipCorrect: the connector consists of the plus part (red) and the minus part (dark grey).
Source: KNX Basic Course Documentation — 10 — p. 110Q24
Where may a KNX bus cable legitimately end?- A.Only inside the power supply unit.
- B.Anywhere convenient, as bare stripped cores.
- C.Only at a bus device or at a bus connector.
- D.At any 230 V mains terminal block.
4. KNX Installation· connectors-and-mounting· EasyCorrect answerC — Only at a bus device or at a bus connector.Learning tipCorrect: the bus cable shall only end either at the device itself or at a bus connector.
Source: KNX Basic Course Documentation — 10 — p. 110Q25
How many bus wires can be connected to each part of the standardized TP bus connector?- A.Up to 8 wires.
- B.Up to 2 wires.
- C.Exactly 1 wire.
- D.Up to 4 wires (6 mm stripped).
4. KNX Installation· connectors-and-mounting· MediumCorrect answerD — Up to 4 wires (6 mm stripped).Learning tipCorrect: up to 4 bus wires, stripped to 6 mm, fit each screwless part.
Source: KNX Basic Course Documentation — 10 — p. 110Q26
For which task is the standardized TP bus connector used?- A.Branching or extending the bus cable and connecting/protecting its ends.
- B.Coupling two lines together (line-coupler function).
- C.Discharging surges to earth (overvoltage protection).
- D.Supplying the 30 V DC bus power.
4. KNX Installation· connectors-and-mounting· EasyCorrect answerA — Branching or extending the bus cable and connecting/protecting its ends.Learning tipCorrect: the connector is used for branching, extending, protecting the bus cable ends and connecting the cable to bus devices.
Source: KNX Basic Course Documentation — 10 — p. 110Q27
What does 'primary protection' mean in the KNX lightning-protection context?- A.Fitting an overvoltage protector directly at each bus device.
- B.Connecting active conductors indirectly to the equipotential bonding bar via lightning current arresters.
- C.The basic 2 kV immunity built into every bus device.
- D.The reverse-polarity keying of the TP bus connector.
4. KNX Installation· protection· MediumCorrect answerB — Connecting active conductors indirectly to the equipotential bonding bar via lightning current arresters.Learning tipCorrect: this indirect connection of active conductors through lightning current arresters is primary protection.
Source: KNX Basic Course Documentation — 11 — p. 111Q28
For primary protection of the 230/400 V AC mains, what minimum nominal discharge current (10/350 us) is required per conductor?- A.2,5 kA.
- B.5 kA.
- C.12,5 kA.
- D.25 kA.
4. KNX Installation· protection· MediumCorrect answerC — 12,5 kA.Learning tipCorrect: at least 12,5 kA (10/350 us) per conductor is required for the mains.
Source: KNX Basic Course Documentation — 11 — p. 112Q29
For primary protection of the KNX bus line, what minimum nominal discharge current (10/350 us) per conductor is required?- A.5 kA.
- B.12,5 kA.
- C.0,25 kA.
- D.2,5 kA.
4. KNX Installation· protection· MediumCorrect answerD — 2,5 kA.Learning tipCorrect: at least 2,5 kA (10/350 us) per conductor is required for the bus line.
Source: KNX Basic Course Documentation — 11 — p. 112Q30
How does loop area relate to lightning-induced surges in a KNX installation?- A.The larger the loop area, the smaller the surge.
- B.Loop area has no effect on surge magnitude.
- C.Only loops smaller than 1 m2 generate surges.
- D.The larger the loop area, the larger the expected peak surge.
4. KNX Installation· protection· MediumCorrect answerD — The larger the loop area, the larger the expected peak surge.Learning tipCorrect: the source states peak surge grows with loop area.
Source: KNX Basic Course Documentation — 13 — p. 114Q31
To what surge voltage (core to earth) is the basic immunity of bus devices tested (IEC 63044-3)?- A.4 kV.
- B.2 kV.
- C.600 V.
- D.350 V.
4. KNX Installation· protection· MediumCorrect answerB — 2 kV.Learning tipCorrect: basic immunity is tested with a 2 kV surge core to earth.
Source: KNX Basic Course Documentation — 14 — p. 115Q32
Which situation is NOT listed by the source as a cause of more significant interference on the bus?- A.Installing bus devices in loops.
- B.Running bus and high-power mains in parallel over a long distance.
- C.Using a certified twisted-pair bus cable of the correct colour.
- D.Bus devices connected to metal walls or central-heating pipes.
4. KNX Installation· protection· MediumCorrect answerC — Using a certified twisted-pair bus cable of the correct colour.Learning tipCorrect: cable certification/colour is not listed as a cause of interference.
Source: KNX Basic Course Documentation — 14 — p. 115Q33
What does the source recommend for bus devices installed on cable ends?- A.No extra measures, because basic immunity is always sufficient.
- B.Primary protection only, via a lightning current arrester.
- C.Removal of the terminating bus connector.
- D.Additional secondary protection (an overvoltage protector).
4. KNX Installation· protection· MediumCorrect answerD — Additional secondary protection (an overvoltage protector).Learning tipCorrect: additional secondary protection should be provided for bus devices on cable ends.
Source: KNX Basic Course Documentation — 15 — p. 115Q34
How is the overvoltage protector with KNX bus connector design classified, and how does it differ from primary protection?- A.It is secondary protection at the devices; primary protection uses lightning current arresters on active conductors.
- B.It is just the bus device's own 2 kV basic immunity.
- C.It is primary protection; secondary protection is the equipotential bonding bar.
- D.It is the same thing as a lightning current arrester.
4. KNX Installation· protection· MediumCorrect answerA — It is secondary protection at the devices; primary protection uses lightning current arresters on active conductors.Learning tipCorrect: the overvoltage protector is secondary protection, distinct from the primary lightning current arresters.
Source: KNX Basic Course Documentation — 16 — p. 116Q35
What minimum nominal discharge current (and impulse shape) must the secondary overvoltage protector provide?- A.At least 2,5 kA (10/350 us).
- B.At least 5 kA (8/20 us).
- C.At least 12,5 kA (10/350 us).
- D.At least 350 A (8/20 us).
4. KNX Installation· protection· MediumCorrect answerB — At least 5 kA (8/20 us).Learning tipCorrect: the overvoltage protector must provide at least 5 kA (8/20 us).
Source: KNX Basic Course Documentation — 16 — p. 116Q36
How is the overvoltage protector connected, and can it branch the bus cable?- A.Only by cutting the bus cable and hard-soldering it in line.
- B.It is the normal way to branch the bus cable into three directions.
- C.Via a conventional bus connector or directly to a bus device; it cannot branch the bus cable.
- D.Only through the 230 V mains terminals.
4. KNX Installation· protection· MediumCorrect answerC — Via a conventional bus connector or directly to a bus device; it cannot branch the bus cable.Learning tipCorrect: it connects with a bus connector or directly to a device, and cannot be used to branch the bus.
Source: KNX Basic Course Documentation — 16 — p. 116Q37
What nominal system voltage does a KNX TP power supply unit produce and monitor?- A.30 V DC
- B.30 V AC
- C.230 V AC
- D.21 V DC
4. KNX Installation· power-supply· EasyCorrect answerA — 30 V DCLearning tipSource: KNX Basic Course Documentation — 5.1 — p. 102Q38
What is the minimum voltage a KNX TP bus device needs for safe operation?- A.12 V DC
- B.21 V DC
- C.30 V DC
- D.24 V DC
4. KNX Installation· power-supply· EasyCorrect answerB — 21 V DCLearning tipCorrect: Bus devices require a minimum of 21 V DC for safe operation.
Source: KNX Basic Course Documentation — 5.1 — p. 102Q39
For at least how long can a KNX power supply unit bridge a short interruption of the mains?- A.1 s
- B.10 ms
- C.100 ms
- D.100 microseconds
4. KNX Installation· power-supply· MediumCorrect answerC — 100 msLearning tipCorrect: The PSU can bridge short power gaps of a minimum of 100 ms.
Source: KNX Basic Course Documentation — 5.1 — p. 102Q40
How is a KNX TP line supplied with bus voltage?- A.One PSU in the installation supplies every line through the couplers
- B.Bus devices are powered directly from the 230 V mains
- C.No PSU is needed if fewer than 21 devices are used
- D.Each line needs its own power supply unit
4. KNX Installation· power-supply· EasyCorrect answerD — Each line needs its own power supply unitLearning tipSource: KNX Basic Course Documentation — 5.1 — p. 102Q41
Why is a KNX TP power supply unit resistant to short circuits?- A.Because it has integrated voltage and current control
- B.Because each bus device has its own fuse
- C.Because the bus is a SELV network
- D.Because it operates from the 230 V mains
4. KNX Installation· power-supply· MediumCorrect answerA — Because it has integrated voltage and current controlLearning tipCorrect: The integrated voltage and current control makes the PSU resistant to short circuits.
Source: KNX Basic Course Documentation — 5.1 — p. 102Q42
Which set of output currents corresponds to available centralized KNX TP power supply units?- A.100, 200 and 400 mA
- B.160, 320, 640 and 1280 mA
- C.1, 2 and 4 A
- D.25, 40 and 80 mA
4. KNX Installation· power-supply· MediumCorrect answerB — 160, 320, 640 and 1280 mALearning tipCorrect: The source lists these as available centralized PSU output currents.
Source: KNX Basic Course Documentation — 5.2 — p. 103Q43
Which statement about the choke in KNX TP power supplies is correct?- A.Every PSU always requires a separate external choke
- B.A choke is only needed on the 230 V mains side
- C.Some PSU types have an integrated choke; others need an additional external choke
- D.Chokes are never used in KNX TP installations
4. KNX Installation· power-supply· MediumCorrect answerC — Some PSU types have an integrated choke; others need an additional external chokeLearning tipCorrect: The source states exactly this.
Source: KNX Basic Course Documentation — 5.2 — p. 103Q44
What determines how many devices can be installed in a KNX TP line?- A.The type of PSU used and the individual power consumption of the devices
- B.Exactly 64 devices, regardless of the PSU
- C.The colour of the bus connector
- D.Only the physical length of the bus cable
4. KNX Installation· power-supply· MediumCorrect answerA — The type of PSU used and the individual power consumption of the devicesLearning tipCorrect: The source states the device count depends on the PSU type and each device's consumption.
Source: KNX Basic Course Documentation — 5.2 — p. 103Q45
On a KNX power supply unit, what does a YELLOW LED indicate?- A.The unit is overloaded, possibly due to a short circuit
- B.The 230 V mains supply has failed
- C.The power supply is active and within its normal operating range
- D.An external voltage higher than 30 V has been applied to the bus side
4. KNX Installation· power-supply· MediumCorrect answerD — An external voltage higher than 30 V has been applied to the bus sideLearning tipCorrect: Yellow indicates an external voltage above 30 V on the bus side.
Source: KNX Basic Course Documentation — 5.2 — p. 104Q46
Under what condition can a single power supply unit feed two lines?- A.When additional current is needed, depending on the load
- B.Always – every PSU feeds exactly two lines
- C.Only if both lines together have fewer than 21 devices
- D.Never – one PSU can only ever feed one line
4. KNX Installation· power-supply· MediumCorrect answerA — When additional current is needed, depending on the loadLearning tipCorrect: The source allows one PSU to feed two lines if extra current is needed and the load permits.
Source: KNX Basic Course Documentation — 6 — p. 105Q47
What is the maximum number of centralized power supply units allowed in one line?- A.One
- B.Two
- C.Three
- D.Unlimited, as long as spacing is kept
4. KNX Installation· power-supply· EasyCorrect answerB — TwoLearning tipCorrect: It is not allowed to have more than two centralized PSUs in one line.
Source: KNX Basic Course Documentation — 6.1 — p. 106Q48
In a distributed power supply, how is the bus powered?- A.By connecting the 230 V mains directly to the bus
- B.By batteries fitted inside every bus device
- C.By several devices on the line, each containing a Decentralized Power Supply Unit (DPSU) with an integrated choke module
- D.By a single large centralized PSU only
4. KNX Installation· power-supply· MediumCorrect answerC — By several devices on the line, each containing a Decentralized Power Supply Unit (DPSU) with an integrated choke moduleLearning tipCorrect: The source describes the bus being powered by devices each containing a DPSU with an integrated choke module.
Source: KNX Basic Course Documentation — 7 — p. 107Q49
How many DPSUs may be mounted in one single bus line (even if it consists of segments)?- A.Up to 8
- B.Up to 2
- C.Up to 16
- D.Up to 64
4. KNX Installation· power-supply· MediumCorrect answerA — Up to 8Learning tipCorrect: Up to 8 DPSUs may be used; more than eight can negatively affect communication.
Source: KNX Basic Course Documentation — 7 — p. 107Q50
Which voltage is used for the KNX TP bus?- A.30 V DC
- B.24 V DC
- C.30 V AC
- D.230 V AC
4. KNX Installation· selv-and-insulation· EasyCorrect answerA — 30 V DCLearning tipSource: KNX Basic Course Documentation — 1.1 — p. 97Q51
What does the abbreviation SELV mean, and what is its key property?- A.Standard Electrical Low Voltage: a circuit that must be bonded to protective earth
- B.Safety Extra Low Voltage: a low-voltage circuit electrically separated from higher voltages and isolated from earth
- C.Secure Ethernet Line Voltage: a data-only supply
- D.Single Ended Low Voltage: a voltage referenced to one mains phase
4. KNX Installation· selv-and-insulation· EasyCorrect answerB — Safety Extra Low Voltage: a low-voltage circuit electrically separated from higher voltages and isolated from earthLearning tipCorrect: This matches the definition given for SELV.
Source: KNX Basic Course Documentation — 1 — p. 96Q52
What is the permitted voltage range in a SELV network?- A.120 V for AC and 50 V for DC
- B.25 V for AC and 60 V for DC
- C.50 V for AC and 120 V for DC
- D.30 V for AC and 30 V for DC
4. KNX Installation· selv-and-insulation· MediumCorrect answerC — 50 V for AC and 120 V for DCLearning tipCorrect: The text lists 50 V for alternating current and 120 V for direct current.
Source: KNX Basic Course Documentation — 1 — p. 96Q53
Below which voltages is NO special protection against direct contact required?- A.50 V AC or 120 V DC
- B.60 V AC or 25 V DC
- C.30 V AC or 30 V DC
- D.25 V AC or 60 V DC
4. KNX Installation· selv-and-insulation· MediumCorrect answerD — 25 V AC or 60 V DCLearning tipCorrect: These are the limits stated for omitting direct-contact protection.
Source: KNX Basic Course Documentation — 1 — p. 96Q54
How must a SELV network be treated with respect to earth?- A.It may not be earthed and is isolated from earth and protective earth conductors
- B.It must be solidly earthed at the power supply
- C.It must be connected to the protective earth of the mains
- D.It must be earthed only in wet rooms
4. KNX Installation· selv-and-insulation· MediumCorrect answerA — It may not be earthed and is isolated from earth and protective earth conductorsLearning tipCorrect: SELV must not be earthed and stays isolated from earth and PE conductors.
Source: KNX Basic Course Documentation — 1.1 — p. 97Q55
May a cable intended for mains installation be used to wire the KNX TP network?- A.Yes, any cable rated for 230 V is suitable for the bus
- B.No, cables intended for mains networks may not be used for TP networks
- C.Yes, provided the cable is green
- D.Yes, but only in dry rooms
4. KNX Installation· selv-and-insulation· EasyCorrect answerB — No, cables intended for mains networks may not be used for TP networksLearning tipCorrect: The documentation prohibits reusing mains cable for TP installation.
Source: KNX Basic Course Documentation — 1.1 — p. 97Q56
What generates the SELV voltage for the KNX TP bus?- A.A direct tap off one mains phase
- B.The earthing system of the building
- C.A power supply with secure mains separation
- D.A battery inside each bus device
4. KNX Installation· selv-and-insulation· MediumCorrect answerC — A power supply with secure mains separationLearning tipCorrect: The documentation states a power supply with secure mains separation generates the SELV voltage.
Source: KNX Basic Course Documentation — 1.1 — p. 97