  1. Q01
    The maximum total cable length of a line segment using certified KNX TP cable is 1000 m.
    TrueFalse
    KNX Installation· Bus cable types, installation & distribution boards· Easy
    Correct answer
    True
    Learning tip

    Only the standardized green KNX TP cable guarantees reliable transmission over the total cable length of the line segment, up to a maximum of 1000 m.

  2. Q02
    What is the maximum number of bus devices per line guaranteed by the certified KNX TP cable?
    • A.256 devices
    • B.128 devices
    • C.64 devices
    • D.1000 devices
    KNX Installation· Bus cable types, installation & distribution boards· Easy
    Correct answer
    A — 256 devices
    Learning tip

    Correct: The standardized cable guarantees a maximum of 256 bus devices per line.

  3. Q03
    In the used wire pair of the KNX bus cable, red is plus and black is minus.
    TrueFalse
    KNX Installation· Bus cable types, installation & distribution boards· Easy
    Correct answer
    True
    Learning tip

    The text states the used wire pair is red for plus and black for minus.

  4. Q04
    The spare wire pair (white/yellow) of the KNX bus cable may be used for which of the following?
    • A.A second KNX TP data signal
    • B.A DC SELV supply, or left with no connection at all
    • C.Voice communication
    • D.A 230 V AC mains supply
    KNX Installation· Bus cable types, installation & distribution boards· Medium
    Correct answer
    B — A DC SELV supply, or left with no connection at all
    Learning tip

    Correct: Permitted uses are no connection at all or a DC SELV supply.

  5. Q05
    How should the shielding of KNX bus cables be treated regarding the equipotential bonding bar?
    • A.It must be bonded to the equipotential bar at every device
    • B.It must be earthed at the power supply only
    • C.It must be connected to the protective earth of the mains
    • D.It may not be connected to the equipotential bonding bar
    KNX Installation· Bus cable types, installation & distribution boards· Medium
    Correct answer
    D — It may not be connected to the equipotential bonding bar
    Learning tip

    Correct: The shielding of the bus cables may not be connected to the equipotential bonding bar.

  6. Q06
    A terminating resistor is not required in a KNX TP installation.
    TrueFalse
    KNX Installation· Bus cable types, installation & distribution boards· Easy
    Correct answer
    True
    Learning tip

    The documentation states plainly that a terminating resistor is not required.

  7. Q07
    On which DIN rails may KNX TP DIN-rail mounted devices be installed in a distribution board?
    • A.Standardized EN 50022 35x7.5 mm DIN rails
    • B.Only proprietary KNX rails supplied by the manufacturer
    • C.EN 50090 15x5 mm rails
    • D.Only earthed metal rails used as the SELV return
    KNX Installation· Bus cable types, installation & distribution boards· Medium
    Correct answer
    A — Standardized EN 50022 35x7.5 mm DIN rails
    Learning tip

    Correct: Any commercial board with EN 50022 35x7.5 mm DIN rails may be used.

  8. Q08
    In a KNX TP installation, the maximum permitted length of a single line segment is 1000 m.
    TrueFalse
    KNX Installation· Checking the installation· Easy
    Correct answer
    True
    Learning tip

    Correct. The physical limits of a KNX TP installation set the maximum length of a line segment at 1000 m.

  9. Q09
    In a KNX TP line, what is the maximum permitted distance between the power supply unit and a bus device?
    • A.700 m
    • B.1000 m
    • C.350 m
    • D.As specified by the manufacturer
    KNX Installation· Checking the installation· Medium
    Correct answer
    C — 350 m
    Learning tip

    Correct: The distance between the power supply unit and a bus device may not exceed 350 m.

  10. Q10
    During the installation check, how should the ends of the bus cables be marked?
    • A.'KNX TP' or 'BUS'
    • B.With '230 V' to warn of the operating voltage
    • C.No marking is required at the cable ends
    • D.With the manufacturer's serial number only
    KNX Installation· Checking the installation· Easy
    Correct answer
    A — 'KNX TP' or 'BUS'
    Learning tip

    Correct: Bus cable ends should be clearly identified as KNX TP by marking them 'KNX TP' or 'BUS'.

  11. Q11
    Which statement about connecting the bus cables of different lines is correct?
    • A.Bus cables from different lines may be connected at the line coupler.
    • B.Bus cables from different lines may never be connected together.
    • C.Bus cables from different lines may be connected if the total length stays under 1000 m.
    • D.Bus cables from different lines must be connected to form a single segment.
    KNX Installation· Checking the installation· Easy
    Correct answer
    B — Bus cables from different lines may never be connected together.
    Learning tip

    Correct: Bus cables from different lines may never be connected together; the check looks for such inadmissible connections.

  12. Q12
    The insulation resistance of the bus cable shall be at least 500 kΩ.
    TrueFalse
    KNX Installation· Checking the installation· Easy
    Correct answer
    True
    Learning tip

    Correct. The insulation resistance of the bus cable shall be at least 500 kΩ.

  13. Q13
    At what test voltage should the insulation resistance of the bus cable be measured?
    • A.250 V DC
    • B.230 V DC
    • C.500 V DC
    • D.21 V DC
    KNX Installation· Checking the installation· Medium
    Correct answer
    A — 250 V DC
    Learning tip

    Correct: The insulation resistance measurement should be carried out at 250 V DC.

  14. Q14
    Why should overvoltage protectors be removed before measuring the insulation resistance of the bus cable?
    • A.Because overvoltage protectors are only fitted on mains cables, never on bus cables.
    • B.So the measurement is not influenced and the overvoltage protector is not damaged.
    • C.To raise the test voltage above 250 V DC.
    • D.Because the protectors must be replaced after every insulation test.
    KNX Installation· Checking the installation· Medium
    Correct answer
    B — So the measurement is not influenced and the overvoltage protector is not damaged.
    Learning tip

    Correct: Overvoltage protectors should always be removed before the test so that the measurement is not influenced and the protector is not damaged.

  15. Q15
    What is the minimum bus voltage that must be measured at the end of each bus cable?
    • A.24 V DC
    • B.29 V DC
    • C.20 V DC
    • D.21 V DC
    KNX Installation· Checking the installation· Medium
    Correct answer
    D — 21 V DC
    Learning tip

    Correct: The bus voltage at each bus cable end should be at least 21 V DC.

  16. Q16
    When the ETS project is handed over, the customer's signature confirms agreement with which of the following?
    • A.Only the total price of the installation.
    • B.All the realized functions, and that the installer's warranty expires with any change to the realized KNX installation.
    • C.That the installer stays liable for any future changes made by others.
    • D.That no project documentation needs to be provided.
    KNX Installation· Checking the installation· Medium
    Correct answer
    B — All the realized functions, and that the installer's warranty expires with any change to the realized KNX installation.
    Learning tip

    Correct: With the signature the customer agrees to all realized functions and that the installer's warranty expires with any change to the installation.

  17. Q17
    In the sequence for checking a KNX installation, which check is carried out immediately after checking the polarity of all bus devices?
    • A.Measuring the insulation resistance of the bus cables
    • B.The visual check of the bus cable-end marking
    • C.Measuring the bus voltage at each bus cable end
    • D.Recording the test results
    KNX Installation· Checking the installation· Medium
    Correct answer
    C — Measuring the bus voltage at each bus cable end
    Learning tip

    Correct: The polarity check is followed by measuring the bus voltage (minimum 21 V) at each bus cable end.

  18. Q18
    In a common installation box with a partition, what clearance and creepage distance does the source require between mains and bus?
    • A.2.5 mm.
    • B.8 mm.
    • C.5.5 mm.
    • D.0.5 mm.
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Medium
    Correct answer
    C — 5.5 mm.
    Learning tip

    Correct: the source requires 5.5 mm clearance and creepage distances.

  19. Q19
    How should flush-mounted bus devices be fixed in the wall box?
    • A.By clamp mounting, which is the normal method for bus devices.
    • B.Screw or clamp mounting; either works equally well.
    • C.By gluing the device into any available box.
    • D.In wall boxes suitable for screw mounting; clamp mounting is usually not possible.
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Easy
    Correct answer
    D — In wall boxes suitable for screw mounting; clamp mounting is usually not possible.
    Learning tip

    Correct: only wall boxes suitable for screw mounting may be used.

  20. Q20
    For the WAGO 243-211 connector: On the standardized KNX TP bus connector, which statement about the two parts is correct?
    • A.The plus part is red and the minus part is black.
    • B.The plus part is red and the minus part is dark grey.
    • C.The plus part is black and the minus part is red.
    • D.Both parts are green, matching the bus cable sheath.
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Medium
    Correct answer
    B — The plus part is red and the minus part is dark grey.
    Learning tip

    In the course, the connector has a red positive part and a dark-grey negative part, as on the WAGO 243-211. Other manufacturers, including ABB for XS/S 1.1, describe the connection as red/black. This naming difference is not a polarity difference: check +/− markings and the product manual instead of claiming that black always means only the cable conductor.

  21. Q21
    Where may a KNX bus cable legitimately end?
    • A.Only inside the power supply unit.
    • B.Anywhere convenient, as bare stripped cores.
    • C.Only at a bus device or at a bus connector.
    • D.At any 230 V mains terminal block.
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Easy
    Correct answer
    C — Only at a bus device or at a bus connector.
    Learning tip

    Correct: the bus cable shall only end either at the device itself or at a bus connector.

  22. Q22
    How many bus wires can be connected to each part of the standardized TP bus connector?
    • A.Up to 8 wires.
    • B.Up to 2 wires.
    • C.Exactly 1 wire.
    • D.Up to 4 wires (6 mm stripped).
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Medium
    Correct answer
    D — Up to 4 wires (6 mm stripped).
    Learning tip

    Correct: up to 4 bus wires, stripped to 6 mm, fit each screwless part.

  23. Q23
    For which task is the standardized TP bus connector used?
    • A.Branching or extending the bus cable and connecting/protecting its ends.
    • B.Coupling two lines together (line-coupler function).
    • C.Discharging surges to earth (overvoltage protection).
    • D.Supplying the 30 V DC bus power.
    KNX Installation· Wall boxes, flush-mounted devices & TP bus connector· Easy
    Correct answer
    A — Branching or extending the bus cable and connecting/protecting its ends.
    Learning tip

    Correct: the connector is used for branching, extending, protecting the bus cable ends and connecting the cable to bus devices.

  24. Q24
    What does 'primary protection' mean in the KNX lightning-protection context?
    • A.Fitting an overvoltage protector directly at each bus device.
    • B.Connecting active conductors indirectly to the equipotential bonding bar via lightning current arresters.
    • C.The basic 2 kV immunity built into every bus device.
    • D.The reverse-polarity keying of the TP bus connector.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    B — Connecting active conductors indirectly to the equipotential bonding bar via lightning current arresters.
    Learning tip

    Correct: this indirect connection of active conductors through lightning current arresters is primary protection.

  25. Q25
    For primary protection of the 230/400 V AC mains, what minimum nominal discharge current (10/350 us) is required per conductor?
    • A.2.5 kA.
    • B.5 kA.
    • C.12.5 kA.
    • D.25 kA.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    C — 12.5 kA.
    Learning tip

    Correct: at least 12.5 kA (10/350 us) per conductor is required for the mains.

  26. Q26
    For primary protection of the KNX bus line, what minimum nominal discharge current (10/350 us) per conductor is required?
    • A.5 kA.
    • B.12.5 kA.
    • C.0.25 kA.
    • D.2.5 kA.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    D — 2.5 kA.
    Learning tip

    Correct: at least 2.5 kA (10/350 us) per conductor is required for the bus line.

  27. Q27
    How does loop area relate to lightning-induced surges in a KNX installation?
    • A.The larger the loop area, the smaller the surge.
    • B.Loop area has no effect on surge magnitude.
    • C.Only loops smaller than 1 m2 generate surges.
    • D.The larger the loop area, the larger the expected peak surge.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    D — The larger the loop area, the larger the expected peak surge.
    Learning tip

    Correct: the source states peak surge grows with loop area.

  28. Q28
    To what surge voltage (core to earth) is the basic immunity of bus devices tested (IEC 63044-3)?
    • A.4 kV.
    • B.2 kV.
    • C.600 V.
    • D.350 V.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    B — 2 kV.
    Learning tip

    Correct: basic immunity is tested with a 2 kV surge core to earth.

  29. Q29
    Which situation is NOT listed by the source as a cause of more significant interference on the bus?
    • A.Installing bus devices in loops.
    • B.Running bus and high-power mains in parallel over a long distance.
    • C.Using a certified twisted-pair bus cable of the correct colour.
    • D.Bus devices connected to metal walls or central-heating pipes.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    C — Using a certified twisted-pair bus cable of the correct colour.
    Learning tip

    Correct: cable certification/colour is not listed as a cause of interference.

  30. Q30
    What does the source recommend for bus devices installed on cable ends?
    • A.No extra measures, because basic immunity is always sufficient.
    • B.Primary protection only, via a lightning current arrester.
    • C.Removal of the terminating bus connector.
    • D.Additional secondary protection (an overvoltage protector).
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    D — Additional secondary protection (an overvoltage protector).
    Learning tip

    Correct: additional secondary protection should be provided for bus devices on cable ends.

  31. Q31
    How is the overvoltage protector with KNX bus connector design classified, and how does it differ from primary protection?
    • A.It is secondary protection at the devices; primary protection uses lightning current arresters on active conductors.
    • B.It is just the bus device's own 2 kV basic immunity.
    • C.It is primary protection; secondary protection is the equipotential bonding bar.
    • D.It is the same thing as a lightning current arrester.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    A — It is secondary protection at the devices; primary protection uses lightning current arresters on active conductors.
    Learning tip

    Correct: the overvoltage protector is secondary protection, distinct from the primary lightning current arresters.

  32. Q32
    What minimum nominal discharge current (and impulse shape) must the secondary overvoltage protector provide?
    • A.At least 2.5 kA (10/350 us).
    • B.At least 5 kA (8/20 us).
    • C.At least 12.5 kA (10/350 us).
    • D.At least 350 A (8/20 us).
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    B — At least 5 kA (8/20 us).
    Learning tip

    Correct: the overvoltage protector must provide at least 5 kA (8/20 us).

  33. Q33
    How is the overvoltage protector connected, and can it branch the bus cable?
    • A.Only by cutting the bus cable and hard-soldering it in line.
    • B.It is the normal way to branch the bus cable into three directions.
    • C.Via a conventional bus connector or directly to a bus device; it cannot branch the bus cable.
    • D.Only through the 230 V mains terminals.
    KNX Installation· Lightning, overvoltage, loops & immunity· Medium
    Correct answer
    C — Via a conventional bus connector or directly to a bus device; it cannot branch the bus cable.
    Learning tip

    Correct: it connects with a bus connector or directly to a device, and cannot be used to branch the bus.

  34. Q34
    What nominal system voltage does a KNX TP power supply unit produce and monitor?
    • A.30 V DC
    • B.30 V AC
    • C.230 V AC
    • D.21 V DC
    KNX Installation· Power supply units, two-line & distributed supply· Easy
    Correct answer
    A — 30 V DC
    Learning tip

    Correct: The PSU produces and monitors the 30 V DC system voltage needed for a KNX TP installation.

  35. Q35
    What is the minimum voltage a KNX TP bus device needs for safe operation?
    • A.12 V DC
    • B.21 V DC
    • C.30 V DC
    • D.24 V DC
    KNX Installation· Power supply units, two-line & distributed supply· Easy
    Correct answer
    B — 21 V DC
    Learning tip

    Correct: Bus devices require a minimum of 21 V DC for safe operation.

  36. Q36
    For at least how long can a KNX power supply unit bridge a short interruption of the mains?
    • A.1 s
    • B.10 ms
    • C.100 ms
    • D.100 microseconds
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    C — 100 ms
    Learning tip

    Correct: The PSU can bridge short power gaps of a minimum of 100 ms.

  37. Q37
    How is a KNX TP line supplied with bus voltage?
    • A.One PSU in the installation supplies every line through the couplers
    • B.Bus devices are powered directly from the 230 V mains
    • C.No PSU is needed if fewer than 21 devices are used
    • D.Each line needs its own power supply unit
    KNX Installation· Power supply units, two-line & distributed supply· Easy
    Correct answer
    D — Each line needs its own power supply unit
    Learning tip

    Correct: The source states each line needs its own PSU to supply its bus devices.

  38. Q38
    Why is a KNX TP power supply unit resistant to short circuits?
    • A.Because it has integrated voltage and current control
    • B.Because each bus device has its own fuse
    • C.Because the bus is a SELV network
    • D.Because it operates from the 230 V mains
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    A — Because it has integrated voltage and current control
    Learning tip

    Correct: The integrated voltage and current control makes the PSU resistant to short circuits.

  39. Q39
    Which set of output currents corresponds to available centralized KNX TP power supply units?
    • A.100, 200 and 400 mA
    • B.160, 320, 640 and 1280 mA
    • C.1, 2 and 4 A
    • D.25, 40 and 80 mA
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    B — 160, 320, 640 and 1280 mA
    Learning tip

    Correct: The source lists these as available centralized PSU output currents.

  40. Q40
    Which statement about the choke in KNX TP power supplies is correct?
    • A.Every PSU always requires a separate external choke
    • B.A choke is only needed on the 230 V mains side
    • C.Some PSU types have an integrated choke; others need an additional external choke
    • D.Chokes are never used in KNX TP installations
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    C — Some PSU types have an integrated choke; others need an additional external choke
    Learning tip

    Correct: The source states exactly this.

  41. Q41
    What determines how many devices can be installed in a KNX TP line?
    • A.The type of PSU used and the individual power consumption of the devices
    • B.Exactly 64 devices, regardless of the PSU
    • C.The colour of the bus connector
    • D.Only the physical length of the bus cable
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    A — The type of PSU used and the individual power consumption of the devices
    Learning tip

    Correct: The source states the device count depends on the PSU type and each device's consumption.

  42. Q42
    On a KNX power supply unit, what does a YELLOW LED indicate?
    • A.The unit is overloaded, possibly due to a short circuit
    • B.The 230 V mains supply has failed
    • C.The power supply is active and within its normal operating range
    • D.An external voltage higher than 30 V has been applied to the bus side
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    D — An external voltage higher than 30 V has been applied to the bus side
    Learning tip

    Correct: Yellow indicates an external voltage above 30 V on the bus side.

  43. Q43
    Under what condition can a single power supply unit feed two lines?
    • A.When additional current is needed, depending on the load
    • B.Always – every PSU feeds exactly two lines
    • C.Only if both lines together have fewer than 21 devices
    • D.Never – one PSU can only ever feed one line
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    A — When additional current is needed, depending on the load
    Learning tip

    Correct: The source allows one PSU to feed two lines if extra current is needed and the load permits.

  44. Q44
    What is the maximum number of centralized power supply units allowed in one line?
    • A.One
    • B.Two
    • C.Three
    • D.Unlimited, as long as spacing is kept
    KNX Installation· Power supply units, two-line & distributed supply· Easy
    Correct answer
    B — Two
    Learning tip

    Correct: It is not allowed to have more than two centralized PSUs in one line.

  45. Q45
    In a distributed power supply, how is the bus powered?
    • A.By connecting the 230 V mains directly to the bus
    • B.By batteries fitted inside every bus device
    • C.By several devices on the line, each containing a Decentralized Power Supply Unit (DPSU) with an integrated choke module
    • D.By a single large centralized PSU only
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    C — By several devices on the line, each containing a Decentralized Power Supply Unit (DPSU) with an integrated choke module
    Learning tip

    Correct: The source describes the bus being powered by devices each containing a DPSU with an integrated choke module.

  46. Q46
    How many DPSUs may be mounted in one single bus line (even if it consists of segments)?
    • A.Up to 8
    • B.Up to 2
    • C.Up to 16
    • D.Up to 64
    KNX Installation· Power supply units, two-line & distributed supply· Medium
    Correct answer
    A — Up to 8
    Learning tip

    Correct: Up to 8 DPSUs may be used; more than eight can negatively affect communication.

  47. Q47
    Which voltage is used for the KNX TP bus?
    • A.30 V DC
    • B.24 V DC
    • C.30 V AC
    • D.230 V AC
    KNX Installation· SELV networks & insulation· Easy
    Correct answer
    A — 30 V DC
    Learning tip

    Correct: The documentation states the voltage used for the KNX TP bus is 30 V DC.

  48. Q48
    What does the abbreviation SELV mean, and what is its key property?
    • A.Standard Electrical Low Voltage: a circuit that must be bonded to protective earth
    • B.Safety Extra Low Voltage: a low-voltage circuit electrically separated from higher voltages and isolated from earth
    • C.Secure Ethernet Line Voltage: a data-only supply
    • D.Single Ended Low Voltage: a voltage referenced to one mains phase
    KNX Installation· SELV networks & insulation· Easy
    Correct answer
    B — Safety Extra Low Voltage: a low-voltage circuit electrically separated from higher voltages and isolated from earth
    Learning tip

    Correct: This matches the definition given for SELV.

  49. Q49
    What is the permitted voltage range in a SELV network?
    • A.120 V for AC and 50 V for DC
    • B.25 V for AC and 60 V for DC
    • C.50 V for AC and 120 V for DC
    • D.30 V for AC and 30 V for DC
    KNX Installation· SELV networks & insulation· Medium
    Correct answer
    C — 50 V for AC and 120 V for DC
    Learning tip

    Correct: The text lists 50 V for alternating current and 120 V for direct current.

  50. Q50
    Below which voltages is NO special protection against direct contact required?
    • A.50 V AC or 120 V DC
    • B.60 V AC or 25 V DC
    • C.30 V AC or 30 V DC
    • D.25 V AC or 60 V DC
    KNX Installation· SELV networks & insulation· Medium
    Correct answer
    D — 25 V AC or 60 V DC
    Learning tip

    Correct: These are the limits stated for omitting direct-contact protection.

  51. Q51
    How must a SELV network be treated with respect to earth?
    • A.It may not be earthed and is isolated from earth and protective earth conductors
    • B.It must be solidly earthed at the power supply
    • C.It must be connected to the protective earth of the mains
    • D.It must be earthed only in wet rooms
    KNX Installation· SELV networks & insulation· Medium
    Correct answer
    A — It may not be earthed and is isolated from earth and protective earth conductors
    Learning tip

    Correct: SELV must not be earthed and stays isolated from earth and PE conductors.

  52. Q52
    May a cable intended for mains installation be used to wire the KNX TP network?
    • A.Yes, any cable rated for 230 V is suitable for the bus
    • B.No, cables intended for mains networks may not be used for TP networks
    • C.Yes, provided the cable is green
    • D.Yes, but only in dry rooms
    KNX Installation· SELV networks & insulation· Easy
    Correct answer
    B — No, cables intended for mains networks may not be used for TP networks
    Learning tip

    Correct: The documentation prohibits reusing mains cable for TP installation.

  53. Q53
    What generates the SELV voltage for the KNX TP bus?
    • A.A direct tap off one mains phase
    • B.The earthing system of the building
    • C.A power supply with secure mains separation
    • D.A battery inside each bus device
    KNX Installation· SELV networks & insulation· Medium
    Correct answer
    C — A power supply with secure mains separation
    Learning tip

    Correct: The documentation states a power supply with secure mains separation generates the SELV voltage.

Want more?

See all KNX Basic modules

Other KNX Basic blocks

KNX Basic course exam questions with answers, by chapter →

CertifBus is an independent tool. KNX Basic is a registered trademark of KNX Association. CertifBus is neither affiliated with nor endorsed by KNX Association or any other official certification body. The questions are simulations for educational purposes and do not guarantee success on the official exam.

Explore the KNX Basic certification
Continue with the full exam
KNX BASIC

Your next study session starts with 10 questions.

Try the questions and explanations without an account. Then choose an access period that fits your preparation.

+1 / −0.5 / 0 official scoringFR·EN·DE interface and explanations€9 from · one-time payment
Newsletter

Keep your KNX preparation moving

We’ll email you when new KNX questions, a guide or a tool is published. No spam.

Unsubscribe in 1 click. No sharing with third parties.